Elk M1 Gold as a PowerHome Controller
You must first set the Elk up as a PowerHome
controller. This can be done from the PowerHome Explorer under
PowerHome|Setup|Controllers. You may connect to the Elk directly using a
serial connection or via ethernet if you have an M1XEP.
After creating the Elk controller, click the "Settings"
button to define the COM port (or IP address and Port) and the Analog Poll
Interval. The Analog Poll Interval determines in seconds, how often
PowerHome will query the Elk for the current value of any input points
defined as analog inputs. You must also use the Elk RM utility to
configure the Elk serial port for 115200 bps or properly configure the
ethernet settings.
PowerHome provides support for all aspects of the Elk
M1 Gold. The Elks lighting devices (X10, Insteon, etc.) are available as
X10 devices in PowerHome. The digital (16 multiple-state) inputs on the
Elk and external boards are available as Multi-State Inputs in the Analog
I/O screen. Alternatively, if you're only interested in the open/close
status of the multi-state inputs, you can define these points as Digital
Inputs in the Digital I/O screen. The Elk digital outputs are
available within PowerHome as Digital Outputs in the Digital I/O screen.
Inputs on the Elk setup as analog inputs are available within PowerHome as
analog inputs in the Analog I/O screen. Elk temperature inputs can be
declared as "Temperature" in the Analog I/O screen. The Elk digital
inputs, if defined as Multi-State Inputs on the analog I/O screen, have a
built in formula that will display appropriate values automatically. You
can however override these built in formulas by declaring your own. All
analog inputs, digital inputs, digital outputs, and lighting devices are
automatically available within the PowerHome Device status screen.
Manipulation and reading of these control points are also available using
appropriate PowerHome functions and macro commands. PowerHome also
supports defining inputs (and triggers) for the Elk "Arm Status", "Arm
State", and "Alarm State". The definition for these points are all
done in the Analog I/O screen.
When defining digital outputs, digital inputs, and
analog inputs, the controller will be the ID of the Elk controller, the
unit will be the board number from 1 to 13 (1 is used for the controls
onboard the Elk), and the point will be the individual device number on
the board from 1 to 16. Temperature inputs will have a unit of 1 for
temperature probes, 2 for keypads, and 3 for thermostats. The point value
for temperature inputs will be from 1 to 16 corresponding with the
available units in each category. There is also an alternative
numbering scheme that is allowed that matches the Elk RM numbering scheme
rather than the unit number / point number method. Using this
method, set the Unit to 0. The Point will then be a value starting
at 1. For example, if you are declaring the 5th input on expansion
board 3, you can use either Unit 3, Point 5 or Unit 0, Point 37.
In order for PowerHome to work properly with the above
Elk controls, you MUST also use the Elk RM configuration software to setup
each control appropriately. This cannot be done from within PowerHome
since the protocol for this configuration is proprietary and is not made
available to developers. This is less painless if using the ethernet
interface since both PowerHome and the Elk RM software will be able to
connect simultaneously rather than just one software at a time.
PowerHome also supports standard triggers for the above
Elk control types. When a digital output changes state either from
programming internal to the Elk or from PowerHome control, a digital
output trigger will be fired. Similarly, when an Elk input changes state,
a PowerHome Multi-State Input trigger or Digital Input trigger will
automatically be fired. When an analog input changes, a PowerHome Analog
Input trigger will be fired. For Elk Temperature devices (Temp Probe,
Keypad, Thermostat), a Temperature trigger will be fired. For
lighting devices, the appropriate X10 In and X10 Out triggers will be
fired.
The standard functions ph_getothervar, ph_setothervar,
ph_getothertimer, and ph_setothertimer may be used to access and update
the Elk Custom values. These values are numbered from 1 to 20. Use the
ph_getothervar and ph_setothervar to access and update custom values that
are either numbers or timers. Use ph_getothertimer and ph_setothertimer to
access custom values that are configured as time of day. For time of day
custom values, pass the data as an integer representing the time. For
example, to pass 9:40 pm, the value should be set to 2140.
PowerHome also supports all of the additional control
features within the Elk. In addition to the standard triggers defined
above, PowerHome will also fire the Generic Controller Trigger for certain
Elk specific functions. These are detailed below:
- System Log Data Update: If Elk Global Programming
Location 35 is enabled, PowerHome will fire the Generic Controller Trigger
with a trigger number of 1 and a trigger value of 1. All of the data contained
within the command will be available in the [TEMP] variables.
- Tasks Change Update: If Elk Global Programming
Location 38 is enabled, the Generic Controller Trigger will be fired with a
trigger number of 2 and a trigger value matching the task number (1 to 32).
- Keypad KeyChange Update: If Elk Global Programming
Location 40 is enabled, the GCT will be fired with a trigger number of 3 and a
trigger value of 1.
- Send Valid User Number and Invalid User Code: The GCT
trigger will be fired with a trigger number of 4 and a trigger value of 1.
- Reply Arming Status Report Data: If Elk Global Programming Location 40
(transmit Keypad keys) is enabled, then the GCT trigger will be fired
with a trigger number of 5 and a trigger value of 1.
Support for the Elk specific control commands is
available using the ph_ctlrcmd and ph_ctlrcmd1 functions. The specific
controller command values and parameters are detailed below. To send an
"Arming Status Request" command, the function would look like:
ph_ctlrcmd1("ELKID",120,0,0,"","",1)
- Arming Status Request - 120. No parms. Seconds
returned in ret1. Data returned in ret3.
- Alarm by Zone Request - 240. No parms. Data returned
in ret3.
- Zone Partition Request - 250. No parms. Data returned
in ret3.
- Zone Bypass Request - 260. Zone in parm1, Area in
parm2, PIN in parm3. Data returned in ret1.
- Request Keypad FUnction Key Illumination Status -
270. Keypad in parm1. Code Req returned in ret1, Illum returned in ret3, Beep
returned in ret4.
- Request PLC Status - 280. Bank in parm1. Data
returned in ret3.
- Request ASCII String Text Descriptions - 290. Type in
parm1, Textnum in parm2. Data returned in ret3.
- Request Thermostat Data - 300. Thermostat in parm1.
Temp returned in ret1, Flags returned in ret2, CoolSP in ret3, HeatSP in ret4.
- Request Temperature Format - 310. Type in parm1,
Device in parm2. Temp returned in ret1.
- Request Temperature Data - 312. No parms. Data
returned in ret3.
- Request Valid User Code Areas - 320. Usercode in
parm3. Areamask returned in ret1, type in ret2, diagnostic in ret3, and
digitstemp in ret4.
- Request Keypad Area Assignment - 330. No parms. Data
returned in ret3.
- Request Keypad Function Keypress - 340. Keypad in
parm1, Keynum in parm2. Data returned in ret3.
- Request Zone Definition - 350. No parms. Data
returned in ret3.
- Request Change User Code - 360. Codenum in parm1,
areamask in parm2, oldcode in parm3, newcode in parm4. Return
data in ret1.
- Manual Refresh of Elk statuses - 1000. 0 in parm1 will retrieve
all statuses, 1 in parm1 will get input zone status, 2 in parm1 will get
output status, 3 in parm1 will get analog status, 4 in parm1 will get temperature
status, 5 in parm1 will get arm status, 6 in parm1 will get variables,
7 in parm1 will get counters. 0 in parm2 will fire triggers as a result of any differences, values >
0 in parm2 will cause triggers to NOT be fired.
In addition to the above Controller commands supported
by the Elk, there are a number of "Queued" commands that are also
available for the Elk. "Queued" commands are normal tasks supported by
controllers such as Send X10, Play IR, and Set Digital. The standard
"Queued" commands such as the ones just listed are available by using the
appropriate PowerHome functions or macro commands (such as ph_x10, ph_ir,
etc). To access the non-standard queued commands supported by the Elk, use
the PowerHome ph_ctlrsq function. An example of arm to away in area 1 with
a usercode of 1234 would be: ph_ctlrsq("ELKCTLRID",121,"1234",1,1).
Details on the Elk specific queued commands are below:
- Arm and Disarm commands - 121. User Code in parm1,
level in parm2, and area in parm3.
- Speak Word at Voice Siren Output - 211. Word index in
parm2.
- Speak Phrase at Voice Siren Output - 212. Phrase
index in parm2.
- Task Activation - 221. Task index in parm2.
- Display Text on LCD Screen - 231. Text in parm1,
Flags in parm2, timeout in parm3.
- Set Thermostat Data - 301. Value in parm1, Tstat in parm2, element in