ph_pid PowerHome formula function
Allows for calculating a PID (Proportional
Integral Derivative) control value
ph_pid ( as_id, ad_setpoint, ad_input, ad_outmin, ad_outmax, ad_p, ad_i, ad_d )
| Argument | Description |
| as_id | String. The ID you would like to use for this particular
PID control loop. If the ID has not been used before, a new entry
is created in the PID table. The ID
can only contain the following characters A-Z, 0-9, _, -, or space characters and must
be 25 characters or less in length |
| ad_setpoint | Double. The SetPoint wish to control to. This
is the desired value you hope to achieve by sequentially applying the
output of repeated calls to this function |
| ad_input | Double. The current value of what you're
trying to control. Ideally, the ad_input value will reach and stabilize at
the ad_setpoint value |
| ad_outmin | Double. The minimum control output adjustment
that the function should return |
| ad_outmax | Double. The maximum control output adjustment
| ad_p | Double. The Proportional constant you wish to use |
| ad_i | Double. The Integral constant you wish to use |
| ad_d | Double. The Derivative constant you wish to use |
Double. Returns the calculated control
output to be applied in an effort for
the ad_input value to
equal the ad_setpoint value. Returns -99999999 if the ID contains invalid characters or
is too long
Use this function to enable PID control
loops. A good explantion of PID control can be found at this Wikipedia entry:
https://en.wikipedia.org/wiki/PID_controller.
This type of control algorithm and feedback loop is typically used
in industrial automation.
• ph_pid("TESTPID",75,70.3,
-4,4,0.3,0.02,0) - Returns a value between
-4
and 4 depending upon currently stored internal values from previous executions of
the function. In this hypothetical example, our setpoint is 75 and
the current value is 70.3 which will likely return a value of 4.
Based upon how that effects the current value, the output will be adjusted accordingly until
equilibrium with each successive call to the function. This example
illustrates the most commonly used control loop of PI (Proportional Integral)
control since the Derivative value is set to
0.